3PAR Expansion
Posted: Tue Feb 25, 2025 11:47 pm
I am hoping that someone can review my plan what I have and provide any suggestions. Did I miss anything or does this look good?
I have a 3PAR 7200 (2 node) with 2 drive enclosures and I am looking to expand this to 4 Drive Enclosures.
I downloaded the "HPE_c04441589_HP 3PAR StoreServ 7000 Series Storage Cabling Configuration Guide A_ Two Node System with.pdf" from [https://support.hpe.com/hpesc/public/do ... =c04441589]
I reviewed the 2 Controller with 2 Drive Enclosure cabling and this matches my current cabling for my 7200 (pg 14)
Current Legend:
(Green) - Page 18
1 - Node 0 DP-1 to Node 2 DP-1
2 - Node 0 DP-2 to Node 1 DP-1
(Red) - Page 18
3 - Node 0 DP-1 to Node 2 DP-1
4 - Node 0 DP-2 to Node 1 DP-1
Then I looked at my future or expanded 2 Controller with 4 Drive Enclosure - pg 25
Future/Expanded Legend:
(Green) - Page 30
1 - Node 0 DP-1 to Node 4 DP-1
2 - Node 0 DP-2 to Node 3 DP-1
3 - Node 1 DP-1 to Node 3 DP-2
4 - Node 2 DP-1 to Node 4 DP-2
(Red)- Page 28
5 - Node 0 DP-1 to Node 2 DP-1
6 - Node 0 DP-2 to Node 1 DP-1
7 - Node 1 DP-2 to Node 3 DP-1
8 - Node 2 DP-2 to Node 4 DP-1
I know that when we start the expansion we need to perform the cable moves & adds to one side (Green or Red) then the other side, so I started with the Green side first and then the Red side, I can't recall if it matters Green or Red first, but I'm thinking it doesn't matter which side we perform the cable moves/adds to first as long as we have dual connectivity in the red side we should be ok to start with the Green side.
I am thinking to perform the following changes, starting with moving and adding the cables for the Green side. Just FYI I have licensing (System is licensed for unlimited disks.)
- use checkhealth to see if 3PAR is OK
- Install/rack the new cages with the new Disks and Power On
- prepare the SAS Cable
- Cable the green side first
(Green Side First)
1. Move [Node 0 DP-1 from Node 2 DP-1] to [Node 4 DP-1]
2. Move [Node 0 DP-2 from Node 1 DP-1] to [Node 3 DP-1]
3. Add [Node 1 DP-1 to Node 3 DP-2]
4. Add [Node 2 DP-1 to Node 4 DP-2]
- use showcage to check
- Cable the red side next
(Red Side)
1. Stays the same - No Change [Node 0 DP-1 to Node 2 DP-1]
2. Stays the same - No Change [Node 0 DP-2 to Node 1 DP-1]
3. Add [Node 1 DP-2 to Node 3 DP-1]
4. Add [Node 2 DP-2 to Node 4 DP-1]
- use showcage to check
- admithw (wait if firmware is applied)
- showpd -c (wait until all chunklets are initiaisized) (showpd command displays configuration information about a system's physical disks. -c Shows chunklet usage information. Any chunklet in a failed disk will be shown as "Fail".) Once the new physical disks are successfully admitted to the system, initialization of the chunklets is automatic. Use the "showpd -c" command to see how many uninitialized chunklets remain on each disk.
- use checkhealth to see if 3PAR is OK
- use tunesys to start leveling
Thanks for any feedback, appreciated
I have a 3PAR 7200 (2 node) with 2 drive enclosures and I am looking to expand this to 4 Drive Enclosures.
I downloaded the "HPE_c04441589_HP 3PAR StoreServ 7000 Series Storage Cabling Configuration Guide A_ Two Node System with.pdf" from [https://support.hpe.com/hpesc/public/do ... =c04441589]
I reviewed the 2 Controller with 2 Drive Enclosure cabling and this matches my current cabling for my 7200 (pg 14)
Current Legend:
(Green) - Page 18
1 - Node 0 DP-1 to Node 2 DP-1
2 - Node 0 DP-2 to Node 1 DP-1
(Red) - Page 18
3 - Node 0 DP-1 to Node 2 DP-1
4 - Node 0 DP-2 to Node 1 DP-1
Then I looked at my future or expanded 2 Controller with 4 Drive Enclosure - pg 25
Future/Expanded Legend:
(Green) - Page 30
1 - Node 0 DP-1 to Node 4 DP-1
2 - Node 0 DP-2 to Node 3 DP-1
3 - Node 1 DP-1 to Node 3 DP-2
4 - Node 2 DP-1 to Node 4 DP-2
(Red)- Page 28
5 - Node 0 DP-1 to Node 2 DP-1
6 - Node 0 DP-2 to Node 1 DP-1
7 - Node 1 DP-2 to Node 3 DP-1
8 - Node 2 DP-2 to Node 4 DP-1
I know that when we start the expansion we need to perform the cable moves & adds to one side (Green or Red) then the other side, so I started with the Green side first and then the Red side, I can't recall if it matters Green or Red first, but I'm thinking it doesn't matter which side we perform the cable moves/adds to first as long as we have dual connectivity in the red side we should be ok to start with the Green side.
I am thinking to perform the following changes, starting with moving and adding the cables for the Green side. Just FYI I have licensing (System is licensed for unlimited disks.)
- use checkhealth to see if 3PAR is OK
- Install/rack the new cages with the new Disks and Power On
- prepare the SAS Cable
- Cable the green side first
(Green Side First)
1. Move [Node 0 DP-1 from Node 2 DP-1] to [Node 4 DP-1]
2. Move [Node 0 DP-2 from Node 1 DP-1] to [Node 3 DP-1]
3. Add [Node 1 DP-1 to Node 3 DP-2]
4. Add [Node 2 DP-1 to Node 4 DP-2]
- use showcage to check
- Cable the red side next
(Red Side)
1. Stays the same - No Change [Node 0 DP-1 to Node 2 DP-1]
2. Stays the same - No Change [Node 0 DP-2 to Node 1 DP-1]
3. Add [Node 1 DP-2 to Node 3 DP-1]
4. Add [Node 2 DP-2 to Node 4 DP-1]
- use showcage to check
- admithw (wait if firmware is applied)
- showpd -c (wait until all chunklets are initiaisized) (showpd command displays configuration information about a system's physical disks. -c Shows chunklet usage information. Any chunklet in a failed disk will be shown as "Fail".) Once the new physical disks are successfully admitted to the system, initialization of the chunklets is automatic. Use the "showpd -c" command to see how many uninitialized chunklets remain on each disk.
- use checkhealth to see if 3PAR is OK
- use tunesys to start leveling
Thanks for any feedback, appreciated